Themen

Cyclohexylamin (CHA) 99,5%: Korrosionshemmer & Wasserbehandlung

Cyclohexylamine (CHA) 99.5% is a primary aliphatic amine supplied as a neutralizing corrosion inhibitor for industrial steam-condensate systems and as an intermediate in formulated water-treatment products. At 101.3 kPa, the product boils at 134.5 °C, freezes at −17.7 °C, and has a density of 0.867 g/cm³ at 20 °C. The aqueous base dissociation constant, pKa, is 10.64 at 25 °C, which provides the alkalinity required to protonate carbonic acid in condensate films. The 99.5% grade is normally certified by capillary gas chromatography; bulk certificates of analysis typically control moisture at ≤0.1 wt% and specify total assay by acid-base titration to confirm product consistency. In closed boiler systems, cyclohexylamine volatilizes with steam, condenses with water, and neutralizes acidic species that depress return-line pH.

PropertyTypical valueBasis/condition
Assay by GC≥99.5%cyclohexylamine basis
Molecular weight99.17 g/molcalculated from formula C₆H₁₃N
Density0.867 g/cm³20 °C, ASTM D4052
Boiling point134.5 °C101.3 kPa
Freezing point−17.7 °Creported literature value
Vapor pressure1.41 kPa25 °C
Flash point, closed cup28 °CASTM D56
Water solubilitymiscibleambient temperature
pKa10.6425 °C, potentiometric

The dominant industrial water-treatment function of CHA 99.5% is not oxygen scavenging or scale inhibition; it is pH neutralization of acidic condensate. The product must therefore be specified alongside a mechanical deaerator and an oxygen scavenger such as catalyzed sodium sulfite or erythorbate. Injection of CHA into feedwater without oxygen control leaves carbon steel vulnerable to oxygen pitting at localized aeration cells. In systems with intermittent standby periods, the amine residual also protects during idle conditions only when oxygen ingress is controlled by external nitrogen blanketing or wet layup procedures.

Why Does Condensate pH Control Fail Without a Volatile Neutralizer?

In a steam-condensate loop, bicarbonate alkalinity in feedwater decomposes under boiler temperature and pressure to form carbon dioxide. The dissolved carbon dioxide partitions into the steam phase and redissolves in the condensate film according to the equilibrium CO₂ + H₂O ⇌ H₂CO₃. This acidification is not adequately buffered by typical soft water; in low-alkalinity condensate, pH can fall below 5.8 without neutralizing amine feed. Cyclohexylamine reacts with carbonic acid to form the soluble cyclohexylammonium bicarbonate/carbonate salt: C₆H₁₃N + H₂CO₃ ⇌ C₆H₁₃NH⁺ + HCO₃⁻. The reaction raises condensate pH and converts aggressive carbonic acid to bicarbonate alkalinity.

Weight-loss coupons conforming to ASTM D2688 placed at remote condensate receivers are the standard method for verifying corrosion control, while linear polarization resistance probes provide supplementary trending. The corrosion rate of carbon steel in condensate is not controlled solely by pH; dissolved oxygen at concentrations above 15 μg/L can initiate oxygen pitting even when the return-line pH is maintained. Neutralizing amines such as CHA do not form a persistent barrier film on carbon steel. Their corrosion-control function depends on continuous alkalinity transport to the condensing liquid film and on oxygen exclusion.

Neat CHA feed is calculated from steam production, condensate return fraction, and measured pH at the terminal condensate receiver. Typical initial settings are back-calculated from a target residual of 3–10 mg/L as cyclohexylamine in returning condensate, although the actual dose must be adjusted with feedwater alkalinity and system losses. The metering pump should be interlocked with feedwater flow or steam production so that a loss in flow stops amine feed; a continuously operated pump without proportional control will overfeed during low-load or turndown periods.

Distribution Ratio, Alkalinity, and Corrosion Kinetics in Two-Phase Steam Systems

The vapor-liquid distribution ratio is the primary selector for neutralizing amines. Cyclohexylamine exhibits a high vapor-phase preference under low-pressure saturation conditions; reported distribution ratios near 4.0 at atmospheric steam pressure mean that more amine leaves the boiler water than remains in the liquid phase. By comparison, morpholine exhibits reported distribution ratios of 0.4–0.7 and diethylaminoethanol near 1.5–1.8. This difference governs which sections of a condensate network receive alkalinity and which remain acidic.

AmineTypical V/L distribution at 0.1 MPapKa at 25 °CNeutralizing capacity
Cyclohexylamine4.010.6410.08 mmol/g
Morpholine0.48.3311.48 mmol/g
Diethylaminoethanol1.79.878.53 mmol/g

Because CHA partitions strongly to the steam, it reaches distant condensate zones more efficiently than morpholine, but it depletes from boiler water. In systems with phosphate or caustic boiler-water pH control, this depletion is tolerable. In systems relying solely on CHA for boiler-water alkalinity, the blowdown and returning condensate may show inconsistent pH control after load changes. A high distribution ratio can create overdose in first condensation zones while remote zones remain acidic until the system reaches steady state; rapid feed adjustment may produce pH oscillation of several tenths of a pH unit in long satellite condensate networks.

The neutralizing capacity of CHA is 10.08 mmol/g based on molecular weight; this is lower than morpholine on a mass basis, so higher mass doses may be required for equivalent alkalinity. The practical consequence is that CHA is often blended with morpholine or diethylaminoethanol to combine near-boiler and far-condensate protection. The blend ratio is adjusted from measured amine residual and pH at multiple condensate sample points, not from a fixed rule.

At the feedwater injection point, the 99.5% product is diluted with demineralized water to a concentration of 5–10 wt% before injection into the deaerator storage section. The neat material has a closed-cup flash point of 28 °C, requiring explosion-proof metering pumps and local exhaust if bulk storage is located in an unventilated building. Carbon steel and 316L stainless steel are acceptable for storage tanks; copper, zinc, aluminum, and galvanized carbon steel are not acceptable because the amine attacks these metals or their oxide films. Pump seals and diaphragm materials should be EPDM or PTFE; natural rubber and neoprene swell in contact with cyclohexylamine and fail at the pump head. Transfer lines and bulk tanks are grounded because the liquid is flammable.

When Low-Pressure Fire-Tube Boilers Receive CHA 99.5%, Condensate Monitoring Must Shift to Continuous pH/Conductivity Analysis

Low-pressure fire-tube boilers operating at 0.1–1.0 MPa often return less than 50% condensate, and the feedwater contains variable bicarbonate alkalinity. In this configuration, pH control at the return line is not adequately captured by manually taken samples because the high distribution ratio of CHA creates a time delay between feed change and condensate pH response. Continuous pH analyzers conforming to ASTM D5128 or equivalent on-line low-conductivity instruments are installed after sample coolers that lower the temperature to 25 °C. Cation conductivity measured downstream of a strong-acid cation exchanger separates amine/carbonate alkalinity effects from chloride and sulfate ingress. A rising cation conductivity with stable pH indicates atmospheric air ingress or carryover of neutralizing amine, not necessarily corrosion control.

Overfeed of CHA elevates condensate pH above 9.8 and can accelerate copper alloy dissolution in systems with brass or copper tubing, particularly when oxygen concentration exceeds 15 μg/L. In systems with copper alloys, total neutralizing amine residual is often capped at 10 mg/L as product; above that value, the risk of copper transport increases. The amine also increases condensate total organic carbon and can interfere with downstream ion-exchange resin beds if condensate is used for demineralized water production.

For low-pressure fire-tube boilers, return-line pH is typically controlled between 8.5 and 9.0, with feedwater pH maintained at 8.0–8.5 after deaeration. Boiler-water alkalinity must be coordinated with phosphate or polymer programs; CHA alone does not control hardness scale. It is a corrosion inhibitor, not a scale inhibitor.

Under FDA 21 CFR 173.310, cyclohexylamine is permitted as a boiler water additive in steam that may contact food; the regulatory text sets maximum dosage and residual conditions. Industrial users must verify that steam used in food processing complies with the specific amine concentration limits of the current regulation. Under the European chemicals framework, cyclohexylamine is registered under REACH, and the extended safety data sheet defines derived no-effect levels and exposure scenarios for water treatment. Occupational exposure guidance in the United States includes an ACGIH TLV-TWA of 10 ppm (41 mg/m³) with skin notation. The material is classified as flammable, corrosive, acute toxic, and aquatic chronic under GHS; the transport designation is UN 2357, Class 3/8, Packing Group II.

Published data for this specific configuration is limited when CHA 99.5% is applied to high-pressure once-through subcritical boilers. At pressures above 6.0 MPa, the vapor-liquid distribution ratio approaches unity for many amines, and the amine contributes to cation conductivity. In such cycles, amine selection is constrained by turbine steam purity requirements and condensate polisher performance. Cyclohexylamine use in these systems is generally restricted to industrial steam generators below turbine-grade purity limits unless the cycle chemistry is explicitly modeled.